Brain fart.....Are shared neutrals allowed? What would you write up for the corrective action?
I should know this, but I've encountered several problems today and I'm too frustrated with the other problems for writing this one up.
Thanks!
|
Chad Dunham
Eagle's Nest Inspections
Home Inspections
203K Consulting
Indoor Air Quality (IAQ) Testing
Radon Testing
Mold Testing
309-323-0252
http://www.peoriailhomeinspections.com |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 11/07/2016 11:52 PM EST
|
Mike Casey
General
![[Avatar]](/images/avatar/1c9ac0159c94d8d0cbedc973445af2da.jpg)
Joined: 06/28/2014 07:21 PM EDT
Messages: 1245
Location: San Diego CA
Offline
|
Chad:
Yes, for a multiwire circuit a neutral is shared. Each 120 volt must originate on bus a and b for the multiwire circuit so only the difference returns on the neutral.
http://ecmweb.com/content/multiwire-branch-circuits-can-be-dangerous
|
Mike Casey
Director of Education
Home Inspection University
www.HomeInspectionUniversity.com
www.MichaelCasey.com |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 11/08/2016 08:17 AM EST
|
Roy Lewis
RockStar!
![[Avatar]](/images/avatar/31fefc0e570cb3860f2a6d4b38c6490d.png)
Joined: 07/01/2014 08:26 AM EDT
Messages: 113
Offline
|
Chad D wrote:Brain fart.....Are shared neutrals allowed? What would you write up for the corrective action?
I should know this, but I've encountered several problems today and I'm too frustrated with the other problems for writing this one up.
Thanks!
Are you referring to double lugging neutrals?
|
1stproinspection.com |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 11/08/2016 09:27 AM EST
|
Chad D
Batman
![[Avatar]](/images/avatar/76dc611d6ebaafc66cc0879c71b5db5c.jpg)
Joined: 06/24/2014 08:55 AM EDT
Messages: 782
Location: Marquette Heights (Peoria) IL
Offline
|
Thanks Mike!
I always appreciate your help.
Roy,
I was not referring to double tapping (lugging). Inside the main panel I had about half as many grounds and neutrals that should have been there. Upon further review, half of the breakers had black wires and the other half have red wires. So that told me there were many shared neutrals. I'm sure I've seen this before, but it's not common that I see it. I have never done that when I have wired a panel.
|
Chad Dunham
Eagle's Nest Inspections
Home Inspections
203K Consulting
Indoor Air Quality (IAQ) Testing
Radon Testing
Mold Testing
309-323-0252
http://www.peoriailhomeinspections.com |
|
 |
![[Post New]](/templates/homeinspectionforum/images/icon_minipost_new.gif) 11/09/2016 09:46 PM EST
|
gfricke
The Big Lebowski
![[Avatar]](/images/avatar/32bb90e8976aab5298d5da10fe66f21d.jpg)
Joined: 06/19/2014 09:51 PM EDT
Messages: 453
Location: St Petersburg, FL
Offline
|
New NEC code mandates shared neutral breakers have handle ties on them
|