Please identify the problems with any unsealed penetrations from floor to floor, and between dwellings at device boxes in multistory dwellings.

Joe Tedesco, NEC Consultant

My statements, written or oral on this site, shall not be considered as the official position of NFPA or any of its Committees, and shall not be considered to be, nor be relied upon as, a Formal Interpretation. They are my personal opinions.
[WWW]
Juan Jimenez
Seal Team 6
[Avatar]

Joined: 06/18/2014 08:53 PM EDT
Messages: 987
Location: Richmond, VA
Offline

Isn't it for draft stopping?

http://www.ahouseonarock.com
http://www.chimneysweeprichmond.com
[WWW]
Joe Tedesco
Wizard
[Avatar]

Joined: 06/19/2014 08:59 AM EDT
Messages: 151
Location: Boston, Massachusetts
Offline

Juan Jimenez wrote:Isn't it for draft stopping?
From the 2011 NECH:

"300.21 Spread of Fire or Products of Combustion

Electrical installations in hollow spaces, vertical shafts, and ventilation or air-handling ducts shall be made so that the possible spread of fire or products of combustion will not be substantially increased. Openings around electrical penetrations into or through fire-resistant-rated walls, partitions, floors, or ceilings shall be firestopped using approved methods to maintain the fire resistance rating.

Informational Note: Directories of electrical construction materials published by qualified testing laboratories contain many listing installation restrictions necessary to maintain the fire-resistive rating of assemblies where penetrations or openings are made. Building codes also contain restrictions on membrane penetrations on opposite sides of a fire-resistance-rated wall assembly. An example is the 600-mm (24-in.) minimum horizontal separation that usually applies between boxes installed on opposite sides of the wall. Assistance in complying with 300.21 can be found in building codes, fire resistance directories, and product listings."

Joe Tedesco, NEC Consultant

My statements, written or oral on this site, shall not be considered as the official position of NFPA or any of its Committees, and shall not be considered to be, nor be relied upon as, a Formal Interpretation. They are my personal opinions.
[WWW]
 