Exhaust vent termination req for gas water heater  XML
Forum Index » Plumbing Systems
Author Message
Kris Svendsen
49er
[Avatar]

Joined: 06/22/2014 08:52 PM EDT
Messages: 337
Location: Dallas, TX
Offline

I'm having trouble locating the information on the termination req for gas water heater? This one seems pretty close to surrounding material. So far I've only found "according to manufacturers recommended installation instruction". Does anyone have more info?
[Thumb - i68.jpg]
 Filename i68.jpg [Disk] Download
 Description
 Filesize 52 Kbytes
 Downloaded:  495 time(s)


Kris Svendsen
Viking Inspections
Professional Real Estate Inspector, TREC #20511
Certified Level III Infrared Thermographer #10829
469-209-8130
http://vikinginspections.com
http://facebook.com/VikingInspections
http://facebook.com/svendsenkris
http://linkedin.com/in/krissvendsen
https://twitter.com/vikinginspect
http://vikinginfrared.com
http://facebook.com/VikingInfrared
[Email] [WWW]
advanced
Expert

Joined: 02/10/2015 04:29 PM EST
Messages: 213
Location: Greenville SC
Offline

I believe the same rules apply to any gas b vented appliance under 12in diameter, obviously under the current scenario backdrafting can occur,
Table of Type B-Vent Rooftop Clearance Requirements

Vent caps larger than 12" must be located at least 2 feet above the highest point and 2 feet higher than any portion of the building within a horizontal distance of 10 feet.

Vent caps 12" and smaller may terminate a distance above the roof if 8 feet or more away from a vertical surface as follows:
Roof Pitch: rise/run in inches Minimum feet above roof surface
Flat to 7/12 1.0 foot above the roof surface
7/12 to 8/12 1.5 feet above the roof surface
8/12 to 9/12 2.0 feet above the roof surface
9/12 to 10/12 2.5 feet above the roof surface
10/12 to 11/12 3.25 feet above the roof surface
11/12 to 12/12 4.0 feet above the roof surface * Continues to 21/12 pitch at 8.0 feet


Stuart Malamut


stuart.malamut@housemaster.com/greenvillesc
Radon Measurement Certification
Licensed in South Carolina and North Carolina
864-641-6180
Serving the Upstate of South Carolina and
Northern Georgia
Greenville / Spartanburg / Anderson Area Regional Director of Housemaster
NIBI Certified
[Email]
Pete Campbell
Jedi
[Avatar]

Joined: 06/18/2014 10:55 PM EDT
Messages: 1590
Location: Fort Pierce, SE Florida
Offline

That's a new cap on an old vent pipe. Kris, did the vent pipe inside the house below the roof look properly located or maybe a homeowner retrofit?

The house does not look too old.

Pete Campbell
Guaranteed Inspections
772-882-9623
ClientCare@GuaranteedInspections.us
http://www.PortStLucieInspections.com
http://www.GuaranteedInspections.us
http://www.GuaranteedInspections.biz



Inspecting Fort Pierce, St. Lucie Village, Lakewood Park, Vero Beach, Indian River Shores, Sebastian, Fellsmere, Fort Drum, Okeechobee, Jensen Beach, Stuart, Palm City, Hobe Sound and Indiantown, Florida.

[Email] [WWW]
Mike Casey
General
[Avatar]

Joined: 06/28/2014 07:21 PM EDT
Messages: 1245
Location: San Diego CA
Offline

IRC 2427.8.4. If there is any vertical surface within 8-feet the B-vent should be 2 feet higher than any part of the building within 10-feet. So it looks incorrect.

Thanks!

Mike Casey
Director of Education
Home Inspection University
www.HomeInspectionUniversity.com
www.MichaelCasey.com